thermionic1
Electrical
- Nov 30, 2018
- 314
It is well established that the North American / ANSI world favors dead tank HV Swgr and the IEC world favors live tank. With that said, I'm curious about the reasons or opinions for these differences. Excluding HV Metering CT/VT.
Consider a 362kV DT Breaker (SF6 Type)
Compare to 400kV Live Tank (SF6 Type)
Is there a significant cost savings? Is one design inherently better / safer? Does seismic activity affect either? Does the SF6 volume matter that much? Is the installation cost a factor?
We recently had an outage in the area and root cause was a failed HV CT. I've read about these issues in Doble conference papers and elsewhere. I can't recall where a bushing CT has violently failed (not caused by human interaction).
Consider a 362kV DT Breaker (SF6 Type)
Single Large Foundation for Tanks & Control Cabinet
Six to 18 600V Class Multi Ratio Bushing CT's
Approx 350 lbs SF6
Some makes require extensive effort to install bushings & vac / fill gas
Six to 18 600V Class Multi Ratio Bushing CT's
Approx 350 lbs SF6
Some makes require extensive effort to install bushings & vac / fill gas
Compare to 400kV Live Tank (SF6 Type)
Three smaller foundations for breaker & Cabinet
Three smaller foundations for bus side CT's
Three smaller foundations for Line/Xfmr side CT's
Approx 100 lbs SF6
Three smaller foundations for bus side CT's
Three smaller foundations for Line/Xfmr side CT's
Approx 100 lbs SF6
Is there a significant cost savings? Is one design inherently better / safer? Does seismic activity affect either? Does the SF6 volume matter that much? Is the installation cost a factor?
We recently had an outage in the area and root cause was a failed HV CT. I've read about these issues in Doble conference papers and elsewhere. I can't recall where a bushing CT has violently failed (not caused by human interaction).