Sahkah

Mechanical
Jan 11, 2019
15
0
0
CA
Hello, I appreciate your help on the following issue regarding the requirement for a booster fire pump and/or a standpipe.
The building , built in the seventies in Toronto , Canada , is an office building , 3 storey and a basement (group D by the NBC) , it has both the basement and first floor sprinklered , plus a standpipe system servicing the whole building. Currently it is equipped with a fire booster pump. The issue here is whether or not this building is over-designed in its fire protection systems. Such that no standpipe system is required , nor the partial sprinkler system (in the basement and first floor) is required and, consequently no requirement for the fire pump . A Standpipe pressure test has been conducted and the city water pressure was only 45 psi with a flow of 100 gpm . The pressure does not meet the requirement of the Ontario building code of 65 psi @ 100 gpm . Would this shortage of pressure be considered to keep the fire pump utilized or is the fire pumper truck pressure is all what this building need to suppress fire ?
Please let me know your thoughts. Thank you
 
Replies continue below

Recommended for you

Not only the fire department but also consult with your commercial insurance company that may have qualified fire protection engineers.
 