Greeting to All,
We have an expansion, and there is a plan to supply a new 35kV bus directly through a cable from an existing 35kV bus. The distance is about 20m and the demand is about 30MVA. So, both bus's will be connected directly through a cable and two CB's (no transformer).

It is a new idea, and I would highly appreciate if you can help to know the impact or precautions to be considered. Also I would like to know wither such connection is accepted by standards or not.

Fyi, majority of load are motor drives.

Thanks in advance for your help.
 
Replies continue below

Recommended for you

This is quite a common arrangement at both 11kV and 33kV for us, particularly where there are space constraints preventing a long switchboard, or where we want to segregate the switchboards for increased security. We use single core cables for the interconnector, and a simple high impedance unit protection scheme to protect the cable link. You might want to consider a mechanical interlocking scheme for earthing the busbar for work, depending on the design of the switchgear and your local safety rules and operational practices.
Regards
Marmite
 