electrageek
Electrical
- Mar 11, 2002
- 116
There is an Industrial Plant with a Gas Turbine Power Plant connected to the same 138Kv substation. The Utility connects via a 15 mile 138Kv transmission line to the existing substations where there are three 70MVA delta connected transformers. Two of the transformers feed the industrial facility and the third connects to the Power Plant. The customer desires to be able to island from the Utility. The Utility end is a grounded wye 138Kv system. My question is, if we island we lose the ground reference supplied by the Utility, can we run without a solid ground reference? The Lighting Arrestors on the Transformers are 88Kv rated. By the way there are three PT's, connected phase to ground in the substation. One set of windings is connected to monitor the zero sequence voltage and trip the Power Plant offline.