I am having an issue on a job with thermal expansion.
The structure is an exterior canopy (open structure - no walls) that utilizes open framing (i.e. all the framing is open below and visible).
The purlins for the roof are 10" tall 18' long 12 ga. cold form C-channels. The client does not want animal issues (such as birds nesting) in the c-channels. As such a 20 ga. cap is being installed to enclose the section and make it appear to be a tube. The cap is a 20 ga plate that is being screwed to the lip of the c-channels at 12" o/c top and bottom with #12 ICC approved self drilling self tapping screws. The screws have an allowable load of over 650lb in shear and over 2,000 lb ultimate. The cap is strictly architectural in nature.
The issue is during temperature swings from day to night of 40 degrees the screws are shearing off at the joint between the cap and the purlin.
Originally we perceived this to be an install issue as the screws were installed with a screws gun with double the rpm's than allowed. However they have been re-installed meeting the requirements of the screw manufacture and failures are still occurring.
The purlin and cap are different gauges; purlin is 12 ga, cap is 20 ga; but are the same material spec. ASTM A653 cold form steel.
Based on our equations the length that a steel member will expand is not conditional on any other property other than the length, thermal expansion coefficient, and temperature swing; change in length = thermal coefficient * length * change in temp.
Based on this should the two members not being expanding the same length together?
Just to be safe after the original issues we calculated the force required to restraining both members from expanding. The equation for this being; force = cross sectional area * modulus of elasticity * coefficient of thermal expansion * temperature swing. Based on that we then took the difference in the forces and determined the number of screws needed and then placed them uniformly through out the connections. The issue is still occurring.
Any ideas on what we might be over looking or doing incorrectly?
The structure is an exterior canopy (open structure - no walls) that utilizes open framing (i.e. all the framing is open below and visible).
The purlins for the roof are 10" tall 18' long 12 ga. cold form C-channels. The client does not want animal issues (such as birds nesting) in the c-channels. As such a 20 ga. cap is being installed to enclose the section and make it appear to be a tube. The cap is a 20 ga plate that is being screwed to the lip of the c-channels at 12" o/c top and bottom with #12 ICC approved self drilling self tapping screws. The screws have an allowable load of over 650lb in shear and over 2,000 lb ultimate. The cap is strictly architectural in nature.
The issue is during temperature swings from day to night of 40 degrees the screws are shearing off at the joint between the cap and the purlin.
Originally we perceived this to be an install issue as the screws were installed with a screws gun with double the rpm's than allowed. However they have been re-installed meeting the requirements of the screw manufacture and failures are still occurring.
The purlin and cap are different gauges; purlin is 12 ga, cap is 20 ga; but are the same material spec. ASTM A653 cold form steel.
Based on our equations the length that a steel member will expand is not conditional on any other property other than the length, thermal expansion coefficient, and temperature swing; change in length = thermal coefficient * length * change in temp.
Based on this should the two members not being expanding the same length together?
Just to be safe after the original issues we calculated the force required to restraining both members from expanding. The equation for this being; force = cross sectional area * modulus of elasticity * coefficient of thermal expansion * temperature swing. Based on that we then took the difference in the forces and determined the number of screws needed and then placed them uniformly through out the connections. The issue is still occurring.
Any ideas on what we might be over looking or doing incorrectly?