JBUDA54
Electrical
- Aug 7, 2001
- 110
Distinguished Forum Members!
I have a 250HP 480V Centrifugal Circulation Pump that supplies water to a Heat Recovery Steam Generator (HRSG) that we have in our specification to Supply an HMCP for short circuit protection and Motor Overloads for Long Time Thermal limit protection. I have been advised by the Eaton Sales Engineer that he has had to swap out HMCPs for High Inertia Loads and High Efficiency Motors due to the high inrush and that a HMCP does not have the flexibility that the thermal magnetic breaker has for the adjust instantaneous settings.
The ABB Baldor Motor is a high efficiency motor that has 1765A Inrush and 276 FLAs. That is slightly less than 6.5 x FLA. Per Eaton the HMCP model number is HMCP600L6CW which has a magnetic trip range of 1800-6000.
The 250HP is also at the top end of the pump curve so this pump could operate at a lower rating
The owner is requesting we spend $10,000 ($5K x 2 (for 2 motors) (approximate price difference between the Thermal magnetic Breaker vs HMCP Breaker)) more for a thermal magnetic breaker scenario because this is a critical motor that needs to not nuisance trip, and have a backup line of protection for the Thermal overloads. I have had other clients direct us to use the thermal magnetic breakers for size 4 and above to bullet proof their facilities so this is not uncommon.
Is it wise to promote to the client to save the $10,000 since the data for the HMCP points to a very feasible design or go with the Thermal magnetic breaker for the above mention requirements?
Keep in mind that the Corporate Elec Engr is the only promoting the Thermal mag breaker and the Project manager is having to answer to the Program Director why we are spending more for the equipment than was estimated at the lower cost.
Your thoughts are greatly appreciated. Thanks in advance.
I have a 250HP 480V Centrifugal Circulation Pump that supplies water to a Heat Recovery Steam Generator (HRSG) that we have in our specification to Supply an HMCP for short circuit protection and Motor Overloads for Long Time Thermal limit protection. I have been advised by the Eaton Sales Engineer that he has had to swap out HMCPs for High Inertia Loads and High Efficiency Motors due to the high inrush and that a HMCP does not have the flexibility that the thermal magnetic breaker has for the adjust instantaneous settings.
The ABB Baldor Motor is a high efficiency motor that has 1765A Inrush and 276 FLAs. That is slightly less than 6.5 x FLA. Per Eaton the HMCP model number is HMCP600L6CW which has a magnetic trip range of 1800-6000.
The 250HP is also at the top end of the pump curve so this pump could operate at a lower rating
The owner is requesting we spend $10,000 ($5K x 2 (for 2 motors) (approximate price difference between the Thermal magnetic Breaker vs HMCP Breaker)) more for a thermal magnetic breaker scenario because this is a critical motor that needs to not nuisance trip, and have a backup line of protection for the Thermal overloads. I have had other clients direct us to use the thermal magnetic breakers for size 4 and above to bullet proof their facilities so this is not uncommon.
Is it wise to promote to the client to save the $10,000 since the data for the HMCP points to a very feasible design or go with the Thermal magnetic breaker for the above mention requirements?
Keep in mind that the Corporate Elec Engr is the only promoting the Thermal mag breaker and the Project manager is having to answer to the Program Director why we are spending more for the equipment than was estimated at the lower cost.
Your thoughts are greatly appreciated. Thanks in advance.