thermal o/l and stalling relays...

Status
Not open for further replies.

ycliff

Electrical
Nov 28, 2003
15
I have a bunch of data for various thermal o/l and stalling relays. can anyone tell me what it all means?

tap:(this is the current tap setting i'm assuming)

time setting: stall:45 (what does this mean? is this just the time setting on the relay like any other relay that goes along w/ the current tap setting above?)

ground: (is the the current tap setting (cts) for the ground ct?) should it have it's own time setting associated with it?

% overload: these are all listed as either 100, 110, 135. is this the % overload of the motor, ie: % of full load amps? does this represent the 50/51 relay (phase time delay and phase instantaneous?) should this have it's own time delay setting?
 
Replies continue below

Recommended for you

Just assumptions, but the 'tap' would indeed be the tap setting for pickup of the overload unit.
I would imagine that a 'stall' setting of 45 would be a time setting to trip upon a stall condition, i.e. LRA for 45 seconds?
'Ground' should be for ground fault current, I'm assuming it's a current setting from your statement. It may have a fixed time delay if there is no setting for it.
'% overload' is interesting if it is on the same relay as 'tap'. It may be a setting based on the tap for overload pickup.
I'm also assuming that you don't have access to any manuals for these relays. Can you tell us manufacturer/model data?
 
Manufacturer/Model:
THERMAL O/L & STALLING RELAY
P&B GOULDS
Mn 5ALI-C53-5
-----------------------------
example:
tap - 74A (FLC of motor)
ct ratio - 100:5
time: curve 1 or 4
% overload - 1.05 * FLC

is the current tap setting = 1.05*(74A)*(5/100)?
 
Are phase inbalance and ground essentially the same thing? ie: does phase inbalance imply that there is a gnd fault somewhere? or are they totally independent?
 
Phase imbalance protection primarily guards against the loss of a phase on a single phase motor.
 
Sorry - make that a "three-phase" motor. Wish this forum had an "edit" function.
 
what is the ct config. for phase inbalance?
 
It looks the the overload pickup setting would be the 'tap' setting times the '% overload' setting, which the relay would see as a ratio from the 100:5A CT. (74A * 1.05 * 5/100 = 3.885A at the relay).

Phase imbalance is not the same as ground fault. Typically, motor protection would be concerned about a voltage imbalance, since a 1% imbalance of the voltage applied to a three-phase motor can cause a 10% current imbalance, and resulting overheating and damage.

As long as there are three CTs for the three-phase, three-wire system, typically in a wye configuration, you can sense current imbalance.
 
ycliff,

phase imbalance and ground fault are totally independent where 5% imbalance voltage will lead to single phase scenario. Thus, phase imbalance relay is required.

I wonder why you dont have realy manuals?

Dandel,
1% imbalance voltage to 10% imbalance current is quite rough,
maybe 1%IV to 5-6%IC is a slim approximation.
GE motor management relay has 10% IC triggers the alarm while 15% IC triggers to trip.
 