Dear Colleagues.
Do we have some standard for the thermal overload curve in digital relays? It's some exponential curve.
I see in many relays eqv.
Teta (termal capacity)=
(I/1.05 x I (FLC/FLA))^2 x (1- e^(t/t(time constant)) x 100%
What is a source of this eqv?
I don't know why, but I think it's BS142 standard.
What is a ANSI/IEEE standard for 49 curves ( if any)?
Thanks for your help.
Regards.
Slava

 
Replies continue below

Recommended for you

I believe that the equation originates from IEC 255-8 (1978). I've seen references to this standard in books illustrating the equation.

See
Also the Areva NPAG Chapter 19 on motor protection has some similar equations and curves illustrated.

Also, the following paper may be of interest:-

Regards
Marmite
 
Dear Marmite.
Thanks a lot.
You are great!!!!!
Today it's IEC60255-8 (1990).
Best Regards.
Slava.

 