nightfox1925
Electrical
- Apr 3, 2006
- 567
I have received a Utility Data for me to model the Utility in the SKM program.
The Data gave me the LLL, LL and LG maximum utility fault contribution. It also specified the "Thevenin Impedance" in X1, R1 and Xo, Ro at 100MVA utility Base. I assume that these impedances are in P.U.
However, if I take the X/R ratio say X1/R1, it equates to 1.2 which is very unlikely for a utility line..so I think I'm not understanding something right.
I put these values on my SKM editor for the Utility and chose the program to consider utility impedance in the calculation and it gave me a 3.7% voltage drop (load flow) at the utility end which is going to cause me a lot of trouble in my main transformer secondary. What I am doubting is if I am using these "Thevenin Impedances" correctly.
The Data gave me the LLL, LL and LG maximum utility fault contribution. It also specified the "Thevenin Impedance" in X1, R1 and Xo, Ro at 100MVA utility Base. I assume that these impedances are in P.U.
However, if I take the X/R ratio say X1/R1, it equates to 1.2 which is very unlikely for a utility line..so I think I'm not understanding something right.
I put these values on my SKM editor for the Utility and chose the program to consider utility impedance in the calculation and it gave me a 3.7% voltage drop (load flow) at the utility end which is going to cause me a lot of trouble in my main transformer secondary. What I am doubting is if I am using these "Thevenin Impedances" correctly.