Minimum condensate drain size:
0-20 tons.... 1"
21-40 tons.... 1-1/4"
41-60 tons.... 1-1/2"
61-100 tons... 2"
101-250 tons... 3"
251 & larger... 4"
AC condensate flow...
Range: 0.02-0.08 GPM/ton
Average: 0.04 GPM/ton
Unitary Packaged AC equipment: 0.006 Gpm/ton
Air Handling Units (100% outside air): 0.100/gpm/1,000 cfm
Air Handling Units (50% outside air): 0.065/gpm/1,000 cfm
Air Handling Units (25% outside air): 0.048/gpm/1,000 cfm
Air Handling Units (15% outside air): 0.041/gpm/1,000 cfm
Pipe size shall not be smaller than drain pan outlet.
Minimum size below grade and below ground floor shall
be 2-1/2". Drain shall have a minimum slope of 1/8"/ft
Verify pipe sizing and discharge requirements with
local authorities and codes.
Depth of trap must exceed by one pipe diameter the
total static pressure of fan.
Try this web site:
Here are some interesting trap details:
You need the 41 inch high trap because you don't want 40 inwg of air pressure to be blowing into your mechanical room.