Buildtech2
Mechanical
- Mar 6, 2012
- 158
thread184-299852
In above thread, TravisMack has posted the following.
"In storage, you are typically going to start with a 8k sprinkler. If the density is >0.34, then you need a 11.2k sprinkler as a minimum".
Can I have any reference for above statement either from NFPA or IBC. I am presently designing a fire protection system for a chemical warehouse which as following information.
1.0 FACILITY DESCRIPTION
Chemical Warehouse
The building is a single story structure constructed of noncombustible material used for storing hazardous and flammable materials in the racking system. The total area of the chemical warehouse is 2024 m² (21786 ft²). The ridge height of warehouse is 7.56 m above the finished floor and eaves height is 6 m.
Tire Store
The building is a single story structure constructed of non-combustible material used for storing automobile tire in bulk quantity. The total area of tire storage is 109 m² (1170 ft²). The height of tire storage is 5.5 m (18 ft.).
2.0 Building Classification
Chemical Warehouse.
As discussed above, the chemicals will be stored in the racking system which are flammable and combustible liquids and solids. These materials readily supports combustion or that pose a physical hazard, therefore these materials shall be classified as Group H-3.
As per NFPA, chemical warehouse was classified as Extra Hazard, Group-2.
Tire Storage.
As per section [F] 903.2.9.2, buildings and structures where the volume for the storage of tires exceeds 20,000 ft² (566 m³) shall be equipped with an automatic sprinkler system in accordance with section 903.3.1.1. As per IBC section [F] 903.2.9.2 Bulk Storage of Tires, the tire store can be classified in Group S-1 occupancy as per IBC. According to this, the buildings and structures where the volume of the tire storage exceeds 20,000 cubic feet (566 m³) shall be equipped throughout with an automatic sprinkler system in accordance with section 903.3.1.1
As per NFPA, tire storage was classified as Ordinary hazard, Group-2.
3.0 Automatic Sprinkler/Gas Suppression Systems
Chemical Warehouse.
As discussed above, the chemicals will be stored in the racking system which are flammable and combustible liquids and solids. These materials readily supports combustion or that pose a physical hazard, therefore these materials shall be classified as Group H-3.
As per IBC, [F] 903.2.5 Group H, an automatic sprinkler system shall be provided in high hazard occupancies.
5.5 Tire Storage.
As per IBC section [F] 903.2.9.2, buildings and structures where the volume for the storage of tires exceeds 20,000 ft² (566 m³) shall be equipped with an automatic sprinkler system in accordance with section 903.3.1.1.
The actual volume of tire storage is 11.7 m x 9.3 m x 5.5 m = 599 m³, therefore an automatic sprinkler system shall be provided in the tire storage room.
In above thread, TravisMack has posted the following.
"In storage, you are typically going to start with a 8k sprinkler. If the density is >0.34, then you need a 11.2k sprinkler as a minimum".
Can I have any reference for above statement either from NFPA or IBC. I am presently designing a fire protection system for a chemical warehouse which as following information.
1.0 FACILITY DESCRIPTION
Chemical Warehouse
The building is a single story structure constructed of noncombustible material used for storing hazardous and flammable materials in the racking system. The total area of the chemical warehouse is 2024 m² (21786 ft²). The ridge height of warehouse is 7.56 m above the finished floor and eaves height is 6 m.
Tire Store
The building is a single story structure constructed of non-combustible material used for storing automobile tire in bulk quantity. The total area of tire storage is 109 m² (1170 ft²). The height of tire storage is 5.5 m (18 ft.).
2.0 Building Classification
Chemical Warehouse.
As discussed above, the chemicals will be stored in the racking system which are flammable and combustible liquids and solids. These materials readily supports combustion or that pose a physical hazard, therefore these materials shall be classified as Group H-3.
As per NFPA, chemical warehouse was classified as Extra Hazard, Group-2.
Tire Storage.
As per section [F] 903.2.9.2, buildings and structures where the volume for the storage of tires exceeds 20,000 ft² (566 m³) shall be equipped with an automatic sprinkler system in accordance with section 903.3.1.1. As per IBC section [F] 903.2.9.2 Bulk Storage of Tires, the tire store can be classified in Group S-1 occupancy as per IBC. According to this, the buildings and structures where the volume of the tire storage exceeds 20,000 cubic feet (566 m³) shall be equipped throughout with an automatic sprinkler system in accordance with section 903.3.1.1
As per NFPA, tire storage was classified as Ordinary hazard, Group-2.
3.0 Automatic Sprinkler/Gas Suppression Systems
Chemical Warehouse.
As discussed above, the chemicals will be stored in the racking system which are flammable and combustible liquids and solids. These materials readily supports combustion or that pose a physical hazard, therefore these materials shall be classified as Group H-3.
As per IBC, [F] 903.2.5 Group H, an automatic sprinkler system shall be provided in high hazard occupancies.
5.5 Tire Storage.
As per IBC section [F] 903.2.9.2, buildings and structures where the volume for the storage of tires exceeds 20,000 ft² (566 m³) shall be equipped with an automatic sprinkler system in accordance with section 903.3.1.1.
The actual volume of tire storage is 11.7 m x 9.3 m x 5.5 m = 599 m³, therefore an automatic sprinkler system shall be provided in the tire storage room.