byzman
Electrical
- May 17, 2002
- 1
I am looking for information on connecting three single phase transformers to make a three phase bank. We requested a 480Y/277 volt service, but utility provided a 120/240 volt service with a center tapped nuetral. The loads are all three phase(there are no 277 volt loads). The primary is connected as WYE (all of the H2 terminals connected), but they are not grounded on the primary side. The primary neutral conductor is only connected to the secondary neutral conductor which runs right to our equipment. It does not appear that the transformer bank is grounded, except through our service grounding electrode. If the 480Y/277 system is better we would like to have it changed, but if there is no difference we do not want to hassle the utility. Any reference materials you could recommend would also be helpful. Thanks.