Had a bit of a "conversation" with an engineer today, regarding his sizing of OCP and wire for a lighting project.
Project involves(2) 100' light poles, with (12) 1000w hps light fixtures on each tower. These are the " Halophane" drop ring style tower and lowering device. The distance is 250' from the 480 3 phase panelboard to the first tower, then 500' more to the last tower. At each tower base, is a backboard with a 60 amp 3 pole 480 v fusible disconnect tapped from the (3) 2/0 copper wire that is run from the main panelboard to the first tower and then on to the 2nd tower.
He calculates the connected load per tower at 25 amps " single phase", because he says that even though the lighting is balanced over 3 phases, the lights themselves are single phase. Or 31.25 at 125%
I calculate the load per tower at roughly 14 amps -3 phase. Becaus the feeder IS 3 phase. Or 17.5 at 125%
As you can see, the difference in these calculations effect everything from wire size, to ocp to disconect size.
Have I been wrong all these years?
HP
HP
Project involves(2) 100' light poles, with (12) 1000w hps light fixtures on each tower. These are the " Halophane" drop ring style tower and lowering device. The distance is 250' from the 480 3 phase panelboard to the first tower, then 500' more to the last tower. At each tower base, is a backboard with a 60 amp 3 pole 480 v fusible disconnect tapped from the (3) 2/0 copper wire that is run from the main panelboard to the first tower and then on to the 2nd tower.
He calculates the connected load per tower at 25 amps " single phase", because he says that even though the lighting is balanced over 3 phases, the lights themselves are single phase. Or 31.25 at 125%
I calculate the load per tower at roughly 14 amps -3 phase. Becaus the feeder IS 3 phase. Or 17.5 at 125%
As you can see, the difference in these calculations effect everything from wire size, to ocp to disconect size.
Have I been wrong all these years?