three single phase transformers impedance matching

Status
Not open for further replies.

k2panman

Electrical
Jun 15, 2004
44
When installing a bank of utility transformers, say 100kVA 25kv:277/480V, using three single phase transformers, what effect does unmatched impedance have on the operation of the bank? If one transformer is 2.0% and the other two are 1.6% for example, what will this do?

K2ofKeyLargo
 
Replies continue below

Recommended for you

You will get unmatched fault currents and unmatched voltage regulation.
 
The transformer bank with unmachet impedance can not be loaded a full capacity.
 
Doesn't this depend on the type of hookup? I was under the impression from some old REA transformer guidelines that the only bank that really had to be watched on this was from a delta/delta connection. I understood that in wye/delta and wye/wye banks it wasn't that much of a concern.
 
Fault current; Divide the full load current by the %impedence to get available fault current. As long as it's less than you equipment rating no problem. If you can safely use three 1.6% transformers, you can use one 1.6% with two 2% transformers.

Voltage regulation.
277 x (1. - .02) = 271.46 volts
277 x (1 - 1.6) = 272.568 volts
difference, = 1.108 volts
One phase will run 1.108 volts higher than the others, the rare time that the incoming phases are exactly equal voltage.
I wouldn't worry.
 