There is a culture with water utilities, that a pit is required for a valve (usually non negotiable). If you step back from the problem & look at the physical requirements from first principle, consider the following: -
* Flexible joints are really dismantling joints, to allow removal of the valve. If valves are only rarely removed, the cost of all of the dismantling joints not used in their lifetime, will more than compensate the cost of cutting a valve out of the pipeline. The only problem is that a dismantling joint is paid for at the time of construction & the cutting out of the valve later in the pipeline life, is paid for by the operations section.
* Keep reducers out of the pit & only have the pipe (equivalent to the valve diameter) in the pit, to keep the pit as small as practical.
* Consider two short spigots with two 150 mm valves on the bypass, that allows the 150 pipework to be replaced without closing the pipeline down (preserve the operation of the main pipeline). Bypasses can have the cement mortar lining stripped during bypass flow, to fill the downstream side of the valve (it depends on how often the bypass is used at full flow - the head loss across the 150 valve is very large resulting in extremely uncontrolled & high flows). Removal of the bends & the short section of 150 pipe is relatively simple with no effect on the integrity of the main pipe flow.
* Chambers are required to protect & maintain the gearing.
* This means that if you only want to operate the gearing, then there is no need for a full depth pit with a floor (see comment below on ground water). I have only on very rare occasions, been able to convince a utility that a 'dirt floor' is sufficient (utility culture).
* A half depth pit is adequate even for the bypass valves. Most bypass valves are about 150 mm diameter & are stock water utility 'buried service valves.'
* I once worked for a major water utility that had a large number of mainline valves from 600 mm to 900 mm diameter (up to 1500 mm pipes). Over a period of 20 years, very few mainline valves were removed & replaced, so it was decided to weld the valves in solid. If a valve is required to be removed, a 'gas axe' (oxycut) will do the job very quickly, especially compared to the time required to empty & refill the pipeline. Two cuts are required close together on one side of the pipe in the pit, remove the short ring, unbolt the valve & remove. A closing band is placed on the pipe, the new valve has the flanged spigot bolted on, lowered into position & bolted on to the flange left in position. The band is pulled back over the short gap & two temporary brackets welded on the band, a bolt used between the two brackets & tightened, the band welded on & a gouging rod used to burn off the temporary brackets. Usually a manhole has been located close to a major valve, allowing reinstatement of the lining.