Hi Lads/Ladies

I'm looking at attaching a supplementary member alongside existing roof rafters to create a cantilevers up to 1200mm. I'm wonder what is the required back span/overlap required. In this instance i have 200mm deep rafters and proposing to stitch 90mm deep overhangs. I wonder at what overlap length the rafters start to act as one. I have seen required back spans such as 1.5xL to 2.0xL (L is the Cantilever)from truss manufacturers. This seems a little excessive as the overhang is being fully supported along the overlap. Are these 1.5 and 2.0xL just guideline and rules of thumb or is there a design or analysis that can be carried out to determine the required overlap length and fixing requirements?

Cheers
AddT
 
Replies continue below

Recommended for you

1200mm seems excessive for 90mm overhangs. In US speak, this is a 4 ft. overhang on 2x4 rafters - which is alot depending on the snow load.
From a connection standpoint, usually going back 1x the cant length is more than sufficient.
 