ContractorDave
Mechanical
- Jan 16, 2007
- 364
I had a discussion with the company president who is a wily fella and our point man on contracts. His take on the last thread regarding NFPA 25's intentions are that systems are still required to be code compliant though specific questions are not asked in the report of all possible conditions. My beef is that 25 will ask if a sprinkler is obstructed, or oriented properly - specific enough questions - but not if the sprinkler installed is of the correct temperature rating for it's location, or whether all sprinklers in a single compartment are QR or SR for example.
We are agreeing to disagree for the moment.
Attached is a pic with numerous problems. The s/w sprinkler is oriented properly is it not? Or does the question assume further: oriented in regards to spacing from the ceiling? Can it be considered a ceiling obstruction because the spray pattern would be fouled by it's proximity to the ceiling? What if it were at 26" instead of 1" (assuming the duct wasn't there)? It's still installed wrong, yet by 25 it passes? The CPVC is installed exposed in a mechanical room. Fail? By 13 yes, by 25 no. The flow switch is not installed per manufacturers requirements. Fail? In this same room is an alarm valve on top of a non-potable connection. Fail? There are other issues like the junction box for the wiring to the control valve tamper has come off the valve and is just dangling there. Ceiling penetrations are not sealed, etc..
Some of this is obviously not within the scope of 13 or a sprinkler systems inspection, and certainly not within the scope of 25 as we have been discussing. Given what / how chapter 5 appears to call violations, there is only: The pipe is not properly supported, and the duct below is an obstruction.
If NFPA 25 isn't the standard to ensure a sprinkler system is installed to code, what is it? I primarily joined this forum so I could ask code related questions and get interpretations and observations from a wide variety of professionals. There have been many posts where a question has begun by myself and others: "I did this inspection and found (this condition) to exist. What is up here?", and invariably, follow up to the post will bring many quotations of various codes and why it isn't the way it's supposed to be. For the installation, it is incorrect, and may not even work. But for 25, as long as there isn't paint on the sprinkler it seems to be ok.
I most certainly think I am missing something in the intent of NFPA 25. Further speculation and input from anyone would be appreciated
Regards
Dave
We are agreeing to disagree for the moment.
Attached is a pic with numerous problems. The s/w sprinkler is oriented properly is it not? Or does the question assume further: oriented in regards to spacing from the ceiling? Can it be considered a ceiling obstruction because the spray pattern would be fouled by it's proximity to the ceiling? What if it were at 26" instead of 1" (assuming the duct wasn't there)? It's still installed wrong, yet by 25 it passes? The CPVC is installed exposed in a mechanical room. Fail? By 13 yes, by 25 no. The flow switch is not installed per manufacturers requirements. Fail? In this same room is an alarm valve on top of a non-potable connection. Fail? There are other issues like the junction box for the wiring to the control valve tamper has come off the valve and is just dangling there. Ceiling penetrations are not sealed, etc..
Some of this is obviously not within the scope of 13 or a sprinkler systems inspection, and certainly not within the scope of 25 as we have been discussing. Given what / how chapter 5 appears to call violations, there is only: The pipe is not properly supported, and the duct below is an obstruction.
If NFPA 25 isn't the standard to ensure a sprinkler system is installed to code, what is it? I primarily joined this forum so I could ask code related questions and get interpretations and observations from a wide variety of professionals. There have been many posts where a question has begun by myself and others: "I did this inspection and found (this condition) to exist. What is up here?", and invariably, follow up to the post will bring many quotations of various codes and why it isn't the way it's supposed to be. For the installation, it is incorrect, and may not even work. But for 25, as long as there isn't paint on the sprinkler it seems to be ok.
I most certainly think I am missing something in the intent of NFPA 25. Further speculation and input from anyone would be appreciated
Regards
Dave