The older thread was closed, but I have a question regarding transfer air as makeup for toilet exhaust. Someone was stating that it is not allowed by code anymore by saying "transfer of room air to another, i.e use of a room as a return plenum is a code violation."
However, does this not fall into the exception the IMC gives you? 601.2 does state "Corridors shall not serve as supply, return, exhaust, relief, or ventilation air ducts" however it also then says "Use of a corridor as a source of makup for toilets, dressing rooms, janitor closets is permitted." So, they clearly recognize that you aren't using transfer air into these spaces as return and rather as makeup air.
My question is this (pretty common scenario I imagine for the senior engineers here):
I have a bathroom that only requires 35cfm of cooling supply air based on the load calculation (only overhead lights and couple people). However, code requires 150CFM of exhaust air out of the space. In an attempt to not over-cool the space, I would prefer to supply 50 and then exhaust 150 by transferring ~100 CFM through the bathroom door. The bathroom is off of the elevator lobby area and has a buffer vestibule. The vestibule and the bathroom itself each have single 3x7 doors with a specified 0.5" gap. This would keep the bathroom a little chilly, but not terrible since it isn't regularly occupied.
The problem is that transferring the 100CFM through the current opening would be around 330 fpm, and while this keeps the door opening force easily under the 30lb requirement, the velocity is still a little higher than I would prefer so I figure I have a couple options.
1)I could overcool the space further and do something like 75CFM supply and 75CFM transfer. The building is set at 77F so, this would essentially bring the bathroom down to a chilly 67F before mixing the transfer air in, leaving the bathroom around 72F which is not bad.
2) I could put a door grille in to allow me to transfer more air without worrying about velocity or door forces. I didn't see any problem with this until I remembered this thread and it had me second-guessing myself again vs the code requirements.
3)I could potentially utilize a series FP VAV to mix plenum air to prevent it from getting too cold in the bathroom while keeping the set supply air.
Obviously I would really like to avoid using reheat since it is electric and seems to be a waste of energy in an unoccupied space like this.
Any suggestions?
The older thread was closed, but I have a question regarding transfer air as makeup for toilet exhaust. Someone was stating that it is not allowed by code anymore by saying "transfer of room air to another, i.e use of a room as a return plenum is a code violation."
However, does this not fall into the exception the IMC gives you? 601.2 does state "Corridors shall not serve as supply, return, exhaust, relief, or ventilation air ducts" however it also then says "Use of a corridor as a source of makup for toilets, dressing rooms, janitor closets is permitted." So, they clearly recognize that you aren't using transfer air into these spaces as return and rather as makeup air.
My question is this (pretty common scenario I imagine for the senior engineers here):
I have a bathroom that only requires 35cfm of cooling supply air based on the load calculation (only overhead lights and couple people). However, code requires 150CFM of exhaust air out of the space. In an attempt to not over-cool the space, I would prefer to supply 50 and then exhaust 150 by transferring ~100 CFM through the bathroom door. The bathroom is off of the elevator lobby area and has a buffer vestibule. The vestibule and the bathroom itself each have single 3x7 doors with a specified 0.5" gap. This would keep the bathroom a little chilly, but not terrible since it isn't regularly occupied.
The problem is that transferring the 100CFM through the current opening would be around 330 fpm, and while this keeps the door opening force easily under the 30lb requirement, the velocity is still a little higher than I would prefer so I figure I have a couple options.
1)I could overcool the space further and do something like 75CFM supply and 75CFM transfer. The building is set at 77F so, this would essentially bring the bathroom down to a chilly 67F before mixing the transfer air in, leaving the bathroom around 72F which is not bad.
2) I could put a door grille in to allow me to transfer more air without worrying about velocity or door forces. I didn't see any problem with this until I remembered this thread and it had me second-guessing myself again vs the code requirements.
3)I could potentially utilize a series FP VAV to mix plenum air to prevent it from getting too cold in the bathroom while keeping the set supply air.
Obviously I would really like to avoid using reheat since it is electric and seems to be a waste of energy in an unoccupied space like this.
Any suggestions?