A tender specification from a well respected consultant recently passed my desk. Part of the requirements under the Variable Speed Drive specification was: "...the VSD's shall be capable of operation without damage for a period of four hours on a 415V +/-25% three phase power supply and any frequency between 25 and 75Hz to minimise potential problems when operating on emergency power supplies and during switching of supplies".
Has anybody seen a spec like this? Not being a generator man myself I'm not sure if gensets are capable of swinging to these extremes. Would the voltage and frequency regulators not shut the system down if this was to occur?
I can calculate the efect of the lower frequencies etc on the DC Link caps but I'm the sort of person to question specs that require products to go out of the normal International specifications. Or is this normal? I've never seen it in the 16 yrs in the VSD business.