Just an FYI on an email I received from NFSA this morning outlining some changes to the FM guidelines:
Travis Mack
MFP Design, LLC
1. There is no maximum size of system. Instead, the “maximum area of coverage for a sprinkler system is limited only by the hydraulic requirements of the sprinkler system’s design for the occupancy being protected” (2-0:2.4.1.6).
2. All system piping must be arranged to drain back to the system’s 2-inch (50 mm) riser drain or auxiliary drain to a safe area. Even for wet pipe systems, piping must be pitched a minimum of ½ in. per 10 ft (4 mm/m) for all branchlines and ¼ in. per 10 ft (2 mm/m) for all other piping. (2-1:2.5.2.4)
3. Unless recommended in 2-0 or a relevant occupancy-related data sheet, no fluid is permitted in a sprinkler system other than water of specific antifreeze solutions addressed in Section 2.4.7 of the data sheet (2-0:2.4.1.9). While a 30% propylene glycol antifreeze solution is allowed for systems exposed to temperatures as low as 25oF (-4oC), data sheet 2-0 calls for the use of a dry pipe system where temperatures can go lower, or for a “refrigerated-area sprinkler system” where temperatures are consistently maintained below 20oF (-7oC). An exception allows the use of other antifreeze solutions for lower temperatures if specifically FM Approved for a temperature 10oF (6oC) below the lowest expected temperature and if the occupancy-specific data sheet allows the use of an antifreeze solution. A second exception allows the typical NFPA 13 antifreeze solutions where the lowest temperature can be below 25oF (-4oC), but only for protected areas not exceeding 2,000 ft2 (185 m2). (2-0:2.4.7.1)
4. In both 2-0 and 8-9 the terms “control mode density area (CMDA)”, “control mode specific application (CMSA)” and “suppression mode” have been eliminated when dealing with different types of sprinklers. There are now only references to “storage”, “nonstorage” and “special protection” sprinklers. This means that FM Global has essentially abandoned the concept of early suppression that led to the development of ESFR sprinklers twenty years ago.
5. System design requirements (number of sprinklers to be included in the design area and minimum densities, flows or pressures) are not contained at all in data sheet 2-0 but are found in occupancy-specific data sheets like 8-9 and 3-26.
6. Data sheet 8-9 been organized to separately deal with five categories of storage:
· Class 1, 2, and 3
· Class 4 and cartoned unexpanded plastics
· Cartoned expanded plastics
· Uncartoned unexpanded plastics
· Uncartoned expanded plastics
Tables for protection of uncartoned expanded plastics in solid pile/palletized/bin-box arrangements contains criteria for protection using only ceiling sprinklers with ceiling heights up to 40 ft (12 m). All protection tables disregard height of storage, and specify design criteria using sprinkler orifice size, minimum number of operating sprinklers and minimum operating pressure. A minimum 3 ft (0.9 m) clearance must be provided between the top of storage and the ceiling-level sprinkler deflectors. Criteria are more liberal for pendent than for upright storage sprinklers.
7. Where ceiling-only sprinklers are provided for rack storage, all transverse flue spaces must be at least 3 in. (75 mm) in net width and must be provided every 4.5 ft (1.4 m) when their net width is less than 6 in. (150 mm) or when vertical alignment of transverse flues cannot be maintained. For well-aligned transverse flues at least 6 in. (150 mm) in net width, spacing of 9 ft (2.7 m) is permitted. Where in-rack sprinklers are provided, transverse flues are not required in the storage tier directly above any level of in-rack sprinklers. Longitudinal flues are not required in are never required in double-row rack storage but, if provided, must be at least 3 in. (754 mm) in net width. (8-9:2.2.2)
8. Upright storage sprinklers are considered tolerant of objects up to 4 in. (100 mm) wide located directly beneath them at any vertical distance, including the pipe on which they are mounted. (2-0: 2.2.3.5.2) In general, obstruction criteria for storage sprinklers resemble that developed for ESFR sprinklers.
9. No area reduction credit is available for the use of high temperature sprinklers. All of the tables in data sheet 8-9 are based on the use of 160oF (70oC) sprinklers for wet systems and 280oF (140oC) sprinklers for dry systems.
10. Rules relative to ceiling slopes have break points at specific angles such as 10o rather than rise in run dimensions.
11. The traditional FM use of a factor of 1.4 times the square root of the design area for determining the length of branch lines is still found within data sheet 3-0 Hydraulics of Fire Protection Systems, but is only required where roof slope exceeds 5 degrees, with a 1.2 factor allowed for slopes equal to or less than 5 degrees. (3-0:2.1.2.2.3.1).
12. Nonstorage occupancies are divided into four hazard classifications:
· HC-1 – includes office, restaurant seating area, unused attics, etc.
· HC-2 – includes parking garages, schools, casinos, etc.
· HC-3 – includes plastics processing, interior loading docks, etc.
· HC-4 – heavily loaded nonstorage areas
Minimum sprinkler orifice sizes are based on the hazard classification and ceiling height. For example, K-5.6 (Km80) sprinklers can be used in HC-1 occupancies with ceiling heights up to 30 ft (9 m), but K-11.2 (Km160) sprinklers must be used if ceilings are 30-60 ft (9-18 m) in height, and K-25.2 (Km360) sprinklers for higher ceilings. (3-26:2.1)
Travis Mack
MFP Design, LLC