I am trying to figure out what the NEC's definition is of a 'torque motor' per NEC(2005)430.6(C).
We have a motor (AC - 3phase) with a torque of 640 ft-lbs which operates at 173RPMs, 30 minute duty. I have never sized conductors for such a motor.
In 430.6(C) they say a torque motor needs to use the locked rotor current in sizing conductors according to 430.22. In 430.22 they don't talk about torque motors (dont expect them too as this just gives percentage of amps to use to size), but they do have a special case for intermittent duty motors(430.22(E)), which is what I have. This section says to use 150% of FLA (table 430.22(E) and short duty- raising/lowering).
So on one hand the torque motor requires 150% of LRA and the intermittent duty requires 150% of FLA for the purposes of sizing conductors. I don't have any other motor nameplate data as of yet so I can't offer more information. Any know which one I should be using? I would hate to have to use 150% of LRA. Thanks for any help.
We have a motor (AC - 3phase) with a torque of 640 ft-lbs which operates at 173RPMs, 30 minute duty. I have never sized conductors for such a motor.
In 430.6(C) they say a torque motor needs to use the locked rotor current in sizing conductors according to 430.22. In 430.22 they don't talk about torque motors (dont expect them too as this just gives percentage of amps to use to size), but they do have a special case for intermittent duty motors(430.22(E)), which is what I have. This section says to use 150% of FLA (table 430.22(E) and short duty- raising/lowering).
So on one hand the torque motor requires 150% of LRA and the intermittent duty requires 150% of FLA for the purposes of sizing conductors. I don't have any other motor nameplate data as of yet so I can't offer more information. Any know which one I should be using? I would hate to have to use 150% of LRA. Thanks for any help.