Toshiba VF-S9 Help
Ryan_Flowers
I have a piece of equipment that requires the use of 5 drive bays pulling a continuous chain. Each drive bay has 2 motors that run off 1 VFD (so 5 VFD's total). Over time each of these VFD's has been changed to a different/newer version. My problem I'm having is that when I go to stop the conveying chain, three of the drives decelerate normally, and two do not. They end up just displaying OFF instead of the frequency dropping. The drive bays controlled by these two VFD's are skipping and damaging components when stopped. I made sure all my basic parameters are the same across the drives with relative accuracy (control, freq reference, ACC, and DEC). I've looked through This manual and can't seem to find a parameter or function that I am missing.
So to be clear, I believe my issue lies with the Toshiba VF-S9 drives displaying OFF instead of decelerating when stopped. Can anyone point me to proper setting to help with my issue?
Thanks!
Here's a couple of thoughts:
1) The deceleration values are not set the same. Some may be set to, say 1sec and the others 10 seconds.
2) There is a separate parameter that states: "Coast to a Stop" which skips the decel action completely.
3) There are now a lot of inputs on drives supposedly for safety that cause drives to remove drive from the output. Even though this could be very dangerous and a hazard to users it seems to be the go to (probably moronic drive lawyers) and the result is always a coast-to-stop. Make sure the correct inputs are actually being used.
4) There are some settings that render decel nonfunctional because of conflicts.
5) Your Toshiba drive has an auto decel parameter that has the drive deciding what the decel should be. This should be turned off.
6) You can have a parameter that is "minimum speed" and the drive can simply coast-to-stop when the speed gets down to that instead of decelling.
That's what comes to mind at the moment. That manual is pretty painful.. :/
Keith Cress
kcress -