hello i have just a general question....

the formula Q=4.5 x CFM x (delta h) i know this is standard formula at sea level but my question that i havent determuned is where does the 4.5 constant get derived from..what are the specifics of that constant and does it change upon ones change in elevation.
 
Replies continue below

Recommended for you

It contains all of the things that are needed to make the units work out.

Things like density, specific heat and 60 are in there.
 
q (btu/hr) = mass flow (lb/hr) x enthalpy change (btu/lb)

mass flow (lb/hr) = volume flow (cf/hr) x density (lb/cf)

60 mins = 1 hour
air density at standard conditions = 0.075 lb/cf

so...

q (btu/hr) = volume flow (cf/min) x 60 (min/hr) x 0.075 (lb/cf) x enthalpy change
or
q = 4.5 x CFM x enthalpy change

altitude, moisture content, and temperature will all affect the 4.5 constant because they all affect density.
 