- May 16, 2019
- 16
How do you deal with the over-sizing of the cooling coil in Trace 700? Do you just assume the higher loads when making the selection? I am fixing cooling coil discharge temp at 55 F and Heating at 85F-90F.
With a VAV reheat system, the program forces heating cfm to always be 30% (default)or what is set as the % cooling minimum. If heating CFM is calculated as 500 cfm, for example, the cooling cfm is forced to be htg cfm/.3 = 1667 CFM regardless of whether 1667 cfm the cfm required for cooling. This results in massive oversizing. I wanted to get input with how everyone here is dealing with this in their equipment selection.
With a VAV reheat system, the program forces heating cfm to always be 30% (default)or what is set as the % cooling minimum. If heating CFM is calculated as 500 cfm, for example, the cooling cfm is forced to be htg cfm/.3 = 1667 CFM regardless of whether 1667 cfm the cfm required for cooling. This results in massive oversizing. I wanted to get input with how everyone here is dealing with this in their equipment selection.