- Jun 24, 2017
- 186
Greetings,
I've done some readings on the topic, but one thing wasn't clear to me and I wanted to get a confirmation on this forum.
Let's consider a hypothetical scenario. We've got a Manual Transfer Switch that has a withstand rating of 65kAIC for the standard 3 cycles per UL 1008, protected upstream by a Circuit Breaker having 100kAIC interrupting rating with instantaneous element enabled. If there is a 70kAIC fault downstream of the switch that is cleared within 3 cycles by the Circuit breaker, does that mean that the MTS was improperly selected for this application and could sustain internal damage by the higher fault current than what it is rated for?
I guess my question is, does the 3-cycle kAIC withstand rating of a transfer switch has to be higher than the maximum available short circuit current downstream of it?
Thanks,
EE
I've done some readings on the topic, but one thing wasn't clear to me and I wanted to get a confirmation on this forum.
Let's consider a hypothetical scenario. We've got a Manual Transfer Switch that has a withstand rating of 65kAIC for the standard 3 cycles per UL 1008, protected upstream by a Circuit Breaker having 100kAIC interrupting rating with instantaneous element enabled. If there is a 70kAIC fault downstream of the switch that is cleared within 3 cycles by the Circuit breaker, does that mean that the MTS was improperly selected for this application and could sustain internal damage by the higher fault current than what it is rated for?