I have a customer with a co-gen plant who wishes to connect to 4160V utility power to use when the generator is down. I am thinking about a manual transfer switch. Would it be more cost effective to utilize standard breakers with relay interlocking to prevent two sources of power to be energized at the same time?
 
Replies continue below

Recommended for you

I would say it would be far cheaper, because even with the transfer switch you would still require these two breakers for protection. (IE - key interlocks between breakers) I've seen cable style interlocks between breakers, but these are less relible, more maintenance, and more easily defeated.
 
If a UL Std 1008 assembly is not required, page 10 of
“…interlocked via means of the operating mechanism, and shall also be equipped with a walking beam interlock to prevent simultaneous closing of both sources during manual operation.

"Kirk-key" circuit-breaker interlocks may be another option.
 