Can anybody have some additional explanation, comments or confirmation regarding the issue below? Thanks in advance..
Transformer: Unindo by Altom (Poyry) T&D
Design Standard: ANSI C57
Power Capacity: 1000kVA, 3 phase, 60Hz
Nominal Voltage: 13.8/0.415kV
Temperature Rise Data:
Winding - 65 deg C
Oil - 60 deg C
Type of Oil - Mineral
Transformer Protection - DGPT
Year of Manufacture: 2000
Actual Data (though limited to 2 days data only)
Peak Load - 548kW
Temperature reading - 70 deg C
The issue is the interpretation of the temperature gauge reading taken, which is 70 deg C with approximately 68-70% loading.
From what I understand, the temperature rise (winding or oil) should not be directly compared to the temperature gauge reading. The temperature gauge reading already includes the ambient or in this case, the room temperature. So if the room temperature is say 28 deg C, the reading of internal transformer temperature is only 42 deg C (70 minus 28).
Considering the above, it is therefore safe to say that there should be no cause for concern reference to the actual temperature reading right?
Notwithstanding, when should the panic alarm be sounded for temperature readings?
Lastly, if in case there is a problem with the temperature, is it technically correct to just provide a radiator fan close to the fins to assist in the cooling process? Does anybody have an idea on how many fans and what size should be considered? Can this be connected to the contacts of the DGPT so that we can set when to start and stop the fans?
Transformer: Unindo by Altom (Poyry) T&D
Design Standard: ANSI C57
Power Capacity: 1000kVA, 3 phase, 60Hz
Nominal Voltage: 13.8/0.415kV
Temperature Rise Data:
Winding - 65 deg C
Oil - 60 deg C
Type of Oil - Mineral
Transformer Protection - DGPT
Year of Manufacture: 2000
Actual Data (though limited to 2 days data only)
Peak Load - 548kW
Temperature reading - 70 deg C
The issue is the interpretation of the temperature gauge reading taken, which is 70 deg C with approximately 68-70% loading.
From what I understand, the temperature rise (winding or oil) should not be directly compared to the temperature gauge reading. The temperature gauge reading already includes the ambient or in this case, the room temperature. So if the room temperature is say 28 deg C, the reading of internal transformer temperature is only 42 deg C (70 minus 28).
Considering the above, it is therefore safe to say that there should be no cause for concern reference to the actual temperature reading right?
Notwithstanding, when should the panic alarm be sounded for temperature readings?
Lastly, if in case there is a problem with the temperature, is it technically correct to just provide a radiator fan close to the fins to assist in the cooling process? Does anybody have an idea on how many fans and what size should be considered? Can this be connected to the contacts of the DGPT so that we can set when to start and stop the fans?