Transformer breakdown

Status
Not open for further replies.

Guardiano

Electrical
Nov 11, 2008
118
Hi,

Something amazing happened to me yesterday. I had to intervence on a motor control centre and the transformer LV side was isolated. The transformer is a 5 MVA 22 k V/ 400 V Dyn11. A few seconds after the 400 V switchgear was opened, the transformer tripped on Bucholz. After verification, we noted that the LV winding was shorted to ground. The insulation of the HV winding is OK as well as the insulation between LV and HV. A di-electric test confirmed that the transformer oil is OK. This transformer was loaded to around 70 % and operated trouble free since it was installed five years ago.
What went wrong?

Guardiano
 
Replies continue below

Recommended for you

I had to intervence on a motor control centre and the transformer LV side was isolated.
I'm not sure what you were doing. Was the transformer de-energized when you were working on the switchgear? Was the switchgear de-energized? Was a breaker or disconnect opened to den-energize the switchgear a few seconds before the transformer trip? Please explain further the circumstances.
 
You may check whether you inadvertently caused a shorting of LV side.Since Buchholz operated,definitely a failure is to be expected. Internal inspection may show you shorting of any LV lead to earth( if you are lucky) or collapse of LV winding to core.
 