- Sep 19, 2013
- 44
I have a 1.5MVA transformer with a 600V secondary. The transformer is a 220 class transformer so 40degC Ambient + 150degC Winding Rise + 30degC Hot Spot = 220degC.
My question is: What temperature ratings do the cables have to be?
If you were to analogously compare a transformer insulation to motor insulation, CECode says Class F/H insulation requires 110degC rated cables.
Does the same apply to transformers? I mean, do the connection points on a transformer rise to 150degC and do I need to be concerned that a 90degC lug or Teck90 cable is inadequate??
Brings me to another point, even if I use 110degC rated cables, I dont know of any compression lugs rated past 90degC.
This temperature rating is always something that I am unsure about.
My question is: What temperature ratings do the cables have to be?
If you were to analogously compare a transformer insulation to motor insulation, CECode says Class F/H insulation requires 110degC rated cables.
Does the same apply to transformers? I mean, do the connection points on a transformer rise to 150degC and do I need to be concerned that a 90degC lug or Teck90 cable is inadequate??
Brings me to another point, even if I use 110degC rated cables, I dont know of any compression lugs rated past 90degC.
This temperature rating is always something that I am unsure about.