Transformer Capacity

Status
Not open for further replies.

Humble2000

Electrical
Nov 17, 2005
132
Based on power quality study which was performed there is a
current THD level of average 7.8% .
Transformer is 500KVA.
I am trying to figure out what would be the derating factor for this transformer.

I have all RMS values for 1-16th harmonics and based on that I am getting k=1.3 which is pretty low!!!

I can not use IEEE 57.110-1986 because I don't have any test data or detail info on transformer.

I know that there is a curve for transformer capacity based on k factor rating,however I belive that is based on loss calculations and...

Any suggestions on this.
Is there any other way of caluclating this
Thanks for all the feedbacks.

 