vtpower
Electrical
- Jan 8, 2005
- 44
Hello All,
I am currently setting up a three phase distribution step-down bank as part of a voltage conversion. This will be three 250KVA Single phase transformers connected ungrounded Y - Delta. My question is, if the impedances of the transformers do not match, I have been told you will only need to de-rate the transformer if they are connected delta-delta, otherwise circultating current will not flow. Is this true, or will I still have circulating current and will I still need to derate the bank in the ungrounded Y - delta connection?
The reason for the ungrounded Y is to not create a grounding bank.
I am currently setting up a three phase distribution step-down bank as part of a voltage conversion. This will be three 250KVA Single phase transformers connected ungrounded Y - Delta. My question is, if the impedances of the transformers do not match, I have been told you will only need to de-rate the transformer if they are connected delta-delta, otherwise circultating current will not flow. Is this true, or will I still have circulating current and will I still need to derate the bank in the ungrounded Y - delta connection?
The reason for the ungrounded Y is to not create a grounding bank.