Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer damage

Status
Not open for further replies.

gmullis195

Electrical
Aug 18, 2017
1
What would be the expected effect on a wye grounded - wye ungrounded transformer if two of the high side bushings were connected to one phase, (example: H1 and H2 connected to Phase A and H3 connected to phase B). Would this be expected to cause ferroresonance as could be expected if the units were single phased? The units in question are 5-leg designs with silicon steel cores feed by 500 feet of underground cable. The units were connected this way for 2+ hours and overheated.

 