Transformer dedicated electrical space?

Status
Not open for further replies.

klubie

Electrical
May 2, 2006
20
NEC 110-26 defines the dedicated electrical space as the width and depth of the equipment and extending from the floor to a height of 6ft above or to structure. I know this applies to panelboards, but does this apply to dry-type transformers, or can an hvac duct be routed over a transformer?
 
Replies continue below

Recommended for you

110.26 is for equipment requiring ready access "while energized". So it will depend on whether or not your application requires that for the dry type transformer.

As for the duct work, if it is used for cooling air, make sure it is insulated (to avoid condensation drip). Also make sure cooling of transformer (air movement) is not impeded, by presence of the duct.

Rafiq Bulsara
 
Thank you!

Does code dictate someplace one application versus another? I could easily say that the unit cannot be serviced "while energized" however that does not mean that the local authority would agree.
 