Transformer Delta Secondary phase grounded

Status
Not open for further replies.

ksavoie

Electrical
Mar 6, 2006
24
I'm doing a project in an old plant where there is a 13.2kv to 480v, 1500kva, delta - delta transformer. The 'B' phase on the secondary is grounded. What advantage or disadvantates of this phase being grouned? Why not just have a floating ground?
 
Replies continue below

Recommended for you

Do a search on this forum for "ungrounded" and you should find lots.
 
What is a floating ground? It's either grounded or it's not. I agree fully with davidbeach, we continue to discuss grounding methods in many threads.
 
Up through the 1950's many industrial power systems were ungrounded. This allowed the system to continue to run on a single fault. Unfortunately, ungrounded systems had problems:
> Arcing to ground could cause fires because the fuse would not blow
> It could be difficult to locate the fault so it would stay on a long time.
> Arcing could cause overvoltages (3x or more)causing other equipment to fail not associated with the first problem.

Rather than replacing their transformers or buying a zig-zag transformer many industrials decided to ground the B phase because it was much cheaper and easier. However there are some differences with B phase grounding that people need to be aware of:
> The voltage of phases A and C to ground are the line to line voltage (e.g. 480) not the "normal" line to neutral voltage so there is a greater shock hazard to people working on the equipment
> Some equipment is not rated for B phase grounding because of the higher voltage to ground
> B phase fuses must be removed and a dummy fuse or bus bar installed in its place, because the NEC in Article 240.22 does not allow a fuse in a grounded conductor. This is because if the B phase fuse were to open and a ground fault existed at the load, current that normally would flow in the B Phase could flow over over the much smaller grounding wire (e.g. a 200 amp load requires a 4/0 phase conductor but only a #6 grounding conductor)
> One advantage of B phase grounding is that because the voltage to ground is higher a ground fault on a large piece of equipment is more likely to clear quickly, especially in an older facilty where they used just conduit and cable tray as the ground fault return path.
 