bdn2004
Electrical
- Jan 27, 2007
- 794
In the Red Book there is this statement about the below circuit.
"It is good practice for transformers of the size shown on the incoming service, where a circuit breaker is used on both the primary and secondary sides, to install percentage differential relays and inverse characteristic overcurrent relays for backup protection. To prevent operation of the differential relays on magnetizing inrush current when energizing the transformer, the large proportion of currents at harmonic multiples of line frequency contained in the magnetizing inrush current are filtered out and passed through the RESTRAINT WINDING so that the current unbalance required to trip is made much greater during the excitation transient than during normal operation."
What is a restraint winding? Has anyone ever seen this happen?
"It is good practice for transformers of the size shown on the incoming service, where a circuit breaker is used on both the primary and secondary sides, to install percentage differential relays and inverse characteristic overcurrent relays for backup protection. To prevent operation of the differential relays on magnetizing inrush current when energizing the transformer, the large proportion of currents at harmonic multiples of line frequency contained in the magnetizing inrush current are filtered out and passed through the RESTRAINT WINDING so that the current unbalance required to trip is made much greater during the excitation transient than during normal operation."
What is a restraint winding? Has anyone ever seen this happen?