Transformer dissolved gases decreasing through time even without degassing 1

Status
Not open for further replies.

chao_david

Electrical
Oct 25, 2017
15
Has anyone encountered this before?

dga_evk0tn.png


This is a 333 kVA 7620/266 single phase transformer. What could be the reason for the decreasing trend? Not sure if its sampling procedure error because majority of the decreasing trend is consistent. I'm not a chemist but my guess that the gas ppm will greatly vary depending if the particular volume of oil you sampled has a huge chunk of gases. But the consistent decreasing trend is bothering me.

Electrical tests such as IR, TTR, Winding resistance, PI, excitation, power factor are ok.
 
Replies continue below

Recommended for you

Many service transformers have atmospheric air exchange, which leads to decreasing combustible gasses over time.

Typically gas concentration in the oil tank becomes evenly distributed within a period of hours. (Sampling procedures generally drain any oil trapped inside the sampling pipe)

The operating temperature of the transformer can impact the H2O concentration, but I am not sure if temperature impacts other gasses.
 
Yes. Such a decrease in gases is not uncommon. Here there was a minor arcing somewhere inside- may be loose core earthing or any current carrying connection. The high level of acetylene indicates such a scenario. The arcing fused and might have disappeared. Hence, the fault is cleared, and there is no more gas generation. The gas level will gradually come down due to breathing out.
 