We have had two (2) new 400/11000 YnD11 step-up transformers, intended to be in parallel operation, that fail primary tests on turns ratio, the test facility are using a Vanguard ATRT-03B tester, and the Results are wildly out.
A - 98, B - 29, C - 18
in addition the instrument says "vector group unknown" - so it cannot establish it
The supplier has produced results which show a consistent 15.88 ratio on all phases but using a single phase ratiometer and testing as follows:
HV side - Neutral and A phase connected. B phase and C phase left open,
LV side - Connect a phase and c phase, b phase leave it open.
They said they Programmed the ratiometer to correct vector group YNd11, and use use formula as HV/(LVxSqrt3) = ratio.,
Questions are:
1. I believe this comes form a field method for testing TX s phase by phase but Anyone got a similar method, or document detailing this procedure - it is not detailed in the BS EN 60079? (sorry, we use EN standards, but happy to have reference to ANSI etc)
2. Why does it seem to pass the above phase by phase method, yet not when all phases are connected and the unit is tested as a three phase transformer using the Vanguard instrument in automatic mode - it is worth noting the unit does not pick up that the TX is a YnD11, and comes up with result unknown?
3. What could this indicate? A mis-configuration on the internal winding connections?
4. What exactly is the prescribed test method over there, ie what do test facilities use - as from what I can see BS EN 60076-1 is pretty vague, section 10.3 does not say much at all?
5. where is it stated you have to use a 3 phase test instrument and not the above / other phase by phase method?
Sorry, a rather long list of questions, but I am a bit lost, and Interested in anyone who has had similar experience, and how the rectification process might go - ultimately we need to be sure these units are right - especially as they will be in parallel operation, and that they are of acceptable quality.
Hopefully someone can answer these and give some technical input as to how this anomaly in the two test can be explained
Many thanks
A - 98, B - 29, C - 18
in addition the instrument says "vector group unknown" - so it cannot establish it
The supplier has produced results which show a consistent 15.88 ratio on all phases but using a single phase ratiometer and testing as follows:
HV side - Neutral and A phase connected. B phase and C phase left open,
LV side - Connect a phase and c phase, b phase leave it open.
They said they Programmed the ratiometer to correct vector group YNd11, and use use formula as HV/(LVxSqrt3) = ratio.,
Questions are:
1. I believe this comes form a field method for testing TX s phase by phase but Anyone got a similar method, or document detailing this procedure - it is not detailed in the BS EN 60079? (sorry, we use EN standards, but happy to have reference to ANSI etc)
2. Why does it seem to pass the above phase by phase method, yet not when all phases are connected and the unit is tested as a three phase transformer using the Vanguard instrument in automatic mode - it is worth noting the unit does not pick up that the TX is a YnD11, and comes up with result unknown?
3. What could this indicate? A mis-configuration on the internal winding connections?
4. What exactly is the prescribed test method over there, ie what do test facilities use - as from what I can see BS EN 60076-1 is pretty vague, section 10.3 does not say much at all?
5. where is it stated you have to use a 3 phase test instrument and not the above / other phase by phase method?
Sorry, a rather long list of questions, but I am a bit lost, and Interested in anyone who has had similar experience, and how the rectification process might go - ultimately we need to be sure these units are right - especially as they will be in parallel operation, and that they are of acceptable quality.
Hopefully someone can answer these and give some technical input as to how this anomaly in the two test can be explained
Many thanks