mbk2k3
Electrical
- Nov 18, 2010
- 97
Good afternoon folks,
I have some questions regarding fault currents and calculating these fault currents for oil-filled transformers:
[ol 1]
[li]When calculating the fault current [full load current / impedance of transformer], do we use full load current at base rating or the full rating with cooling fans running?
[/li]
[li]Are limitations of fault current that a transformer can withstand according to C57.12.00 (Section 7) based on external faults only?[/li]
i.e. full load current / impedance = fault current transformer can withstand for external faults only?
i.e. if a transformer winding failed, its probably going to generate fault currents higher than this FLA/impedance value depending on utility contribution and where the fault is in the windings?
[/ol]
I have some questions regarding fault currents and calculating these fault currents for oil-filled transformers:
[ol 1]
[li]When calculating the fault current [full load current / impedance of transformer], do we use full load current at base rating or the full rating with cooling fans running?
[/li]
[li]Are limitations of fault current that a transformer can withstand according to C57.12.00 (Section 7) based on external faults only?[/li]
i.e. full load current / impedance = fault current transformer can withstand for external faults only?
i.e. if a transformer winding failed, its probably going to generate fault currents higher than this FLA/impedance value depending on utility contribution and where the fault is in the windings?
[/ol]