We have a double-ended substation with 2 ea.- 2000kVA transformers, main breakers and a tie-breaker on the secondary side. Each transformer is currently fed with a 350MCM cable from different sources.
Our plant is now closed, but this substation will stay forever (superfund site). The loads on each side are less than 200kW and there is zero chance of the loads increasing.
The source supplying transformer A is going away. I could move the loads from the A side to the B side; I could run another feed (.25 miles on poles) from the same sub as the B is fed from.
Or to retain the flexibility of having 2 transformers, I could use the same feed as the B transformer by installing a jumper from the line side of the B transformer disconnect switch to the line side of the A transformer disconnect switch. The 350MCM cable would be large enough for the total loads on both transformers. Is there any thing in the code that would allow me to do this?
Our plant is now closed, but this substation will stay forever (superfund site). The loads on each side are less than 200kW and there is zero chance of the loads increasing.
The source supplying transformer A is going away. I could move the loads from the A side to the B side; I could run another feed (.25 miles on poles) from the same sub as the B is fed from.
Or to retain the flexibility of having 2 transformers, I could use the same feed as the B transformer by installing a jumper from the line side of the B transformer disconnect switch to the line side of the A transformer disconnect switch. The 350MCM cable would be large enough for the total loads on both transformers. Is there any thing in the code that would allow me to do this?