Here is one of the downsides of deregulation. I'm a steam guy that needs to provide data to our Independant System Operator on GSU Transformers. There used to be a whole department of knowledgeable electrical engineers across the hall, but with FERC 888 and 889, we can't talk.
Here is my problem. I need to provide impedance data (R and X) at 100 MVA Base for GSUs ranging fron 5MVA to 700MVA. I have the test reports so I can get the following:
Nameplate Voltage, H & X
Load loss watts
Test MVA
% impedance
I think that is all I need to get nominal resistance and reactance, but I could be wrong. If that data is sufficient could someone show me the formulas needed?