- Jul 24, 2019
- 1
Hello
I specified two transformers (5 MVA and 1 MVA) with a transformer impedance not to exceed 6.5 % and 5.75 %. The impedance we got on the two (2) transformers were 5.81 % and 5.09 % respectively, which is below the -7.5 % ANSI min tolerance level.
Is it correct to think that even though I specified the transformer impedance at 6.5 % (Max) and 5.75 % (Max), the vendor is still supposed to meet the minimum negative tolerance (-7.5%) per ANSI.
Thanks for your help in advance.