Is there a rule of thumb as to figuring out what the inductance and resistance should be in a transformer for a given power rating [kVA or MVA], turns ratio, and may be voltages?

I heard there is this 5% or 10% rule. I am putting together a model but Manufacturers don't usually give you the specs on inductance and resistances.
 
Replies continue below

Recommended for you

There are recommended impedances in the ANSI standards for power transformers. The impedance is almost entirely inductive. Impedance is a function of the transformer voltage (BIL) and size (as a first approximation). It can vary quite a bit.

The IEEE Red Book has typical values of impedance and X/R for various types and sizes of transformers - that would be a good starting point.

But no, there is no one-size fits all method to estimate transformer impedance based only on the kVA rating.

Hope that helps.
 