We loaded the 75MVA transformer up to .92PU and performed infrared scanning and meantime observed changes of top oil and winding hottest spot temperature gauge.
4 hours after the uploading, the top oil and winding hottest spot readings are 51C and 71C respectively. It's consistent with the heat run calculation based on IEEE 57.91. But the the infrared showed that the hottest spot was at the lower part of the tank (at the side), it's 84C, while infrared readings of other parts were less than 45C.
The ambient temperature at the time of testing was about 60F, and it's overcast.
I thnik in the normal situation, the the infrared scanning temperature reading should be less than the winding hottest spot temperature reading.
I would like to hear your opinion.
THanks
4 hours after the uploading, the top oil and winding hottest spot readings are 51C and 71C respectively. It's consistent with the heat run calculation based on IEEE 57.91. But the the infrared showed that the hottest spot was at the lower part of the tank (at the side), it's 84C, while infrared readings of other parts were less than 45C.
The ambient temperature at the time of testing was about 60F, and it's overcast.
I thnik in the normal situation, the the infrared scanning temperature reading should be less than the winding hottest spot temperature reading.
I would like to hear your opinion.