Hello
The question : Those anyone had found reference that review, confirmed, explore, challenge, anylize further the statements of that S&C paper about transformer inrush current?
The case :
In one of my last project lately, I do the analysis of the distribution grid for a mining operation site. The utility feed the site with a lenghtly 25 kV line. The mining site is about 30 km away from nearest populated area. The utility substation that feed the mining site was design to mainly feed residential and little commercial loads.
So we end with the utility able the provide a 750 A to 900 A short-circuit capacity at 25 kV for around 32 MVA to 39 MVA.
The main step down transformer of the mining operations site is a 5 MVA 25kV/4160V for In = 115 A. By using the common rule of thumb for Inrush current being 12xIn = 1386 A. Thats over the max short-circuit capacity the utility can provide. So the max Inrush current possible is (real actual data) 785A. Thats about 785/115 = 6.8 time the transformer In.
Later I find this paper on S&C website aboute sizing overcurrent primary protection to withstand inrush current of protection.
That paper suggest a graphical estimation method of the inrush current with transformer powet rating and utility short-circuit capacity. Using this method for my case, I end up with inrush current would be 3xIn.
Since it was the first time that we applied limitations to inrush current for transformer overcurrent protection, we choose to size the protection rating according to an inrush current equal to utility capacity (6.8 x In).
Applying this method bring a lot more flexibility for coordination of protection device. But I would like to find more solid study about it.
The question : Those anyone had found reference that review, confirmed, explore, challenge, anylize further the statements of that S&C paper about transformer inrush current?
The case :
In one of my last project lately, I do the analysis of the distribution grid for a mining operation site. The utility feed the site with a lenghtly 25 kV line. The mining site is about 30 km away from nearest populated area. The utility substation that feed the mining site was design to mainly feed residential and little commercial loads.
So we end with the utility able the provide a 750 A to 900 A short-circuit capacity at 25 kV for around 32 MVA to 39 MVA.
The main step down transformer of the mining operations site is a 5 MVA 25kV/4160V for In = 115 A. By using the common rule of thumb for Inrush current being 12xIn = 1386 A. Thats over the max short-circuit capacity the utility can provide. So the max Inrush current possible is (real actual data) 785A. Thats about 785/115 = 6.8 time the transformer In.
Later I find this paper on S&C website aboute sizing overcurrent primary protection to withstand inrush current of protection.
That paper suggest a graphical estimation method of the inrush current with transformer powet rating and utility short-circuit capacity. Using this method for my case, I end up with inrush current would be 3xIn.
Since it was the first time that we applied limitations to inrush current for transformer overcurrent protection, we choose to size the protection rating according to an inrush current equal to utility capacity (6.8 x In).
Applying this method bring a lot more flexibility for coordination of protection device. But I would like to find more solid study about it.