An earlier thread talked about selecting a high side for to protect a single transformer from inrush. It referred to 12 X normal at 0.1 seconds and 25 X normal at 0.01 seconds.
I'm looking at a case where you have 5 identical kVA transformers (medium voltage) arranged in a daisy chain fashion. Each transformer is spaced out approximately 500 to 1000 ft apart. You have one branch fuse to protect the group of 5 transformers. How do you size that branch fuse?
There are smaller individual fuses for each transformer to isolate them in case of short circuit failures so we can ignore them for this issue.
My first approach was to add up all the transformer kVAs to get one equivalent transformer. I suspect that applying the 12 X and 25 X factors at the 0.1 and 0.01 s points would be too conservative and the resulting fuse would probably be too large. Does anyone have experience doing something like this? If so, what multiples of full load were used for the 0.1 and 0.01 second inrush points?
I suspect some of the wind farms have run into this issue.
I'm looking at a case where you have 5 identical kVA transformers (medium voltage) arranged in a daisy chain fashion. Each transformer is spaced out approximately 500 to 1000 ft apart. You have one branch fuse to protect the group of 5 transformers. How do you size that branch fuse?
There are smaller individual fuses for each transformer to isolate them in case of short circuit failures so we can ignore them for this issue.
My first approach was to add up all the transformer kVAs to get one equivalent transformer. I suspect that applying the 12 X and 25 X factors at the 0.1 and 0.01 s points would be too conservative and the resulting fuse would probably be too large. Does anyone have experience doing something like this? If so, what multiples of full load were used for the 0.1 and 0.01 second inrush points?
I suspect some of the wind farms have run into this issue.