buddy91082
Electrical
- Jan 22, 2009
- 169
I just reviewed a coordination study with a 750kVA transformer (5kv primary - 208Y/120v secondary. The primary protection is a 125E fuse. The coordination curves shows the transformer inrush trippng the 125E fuses. The trip is just on the border line of the fuse melting band.
If i use a 150E fuse the inrush is no longer a problem but the transforer damage curve is worse and arc flash hazard increases a level.
My thought is that the inrush will not occur all the time and is only a theortical value that has the potential to occur. Is there any industry standard i can reference to make a decison on which to sacrifice (nusiance inrush tripping or arc flash and transformer damage). Replacing the 5kv fuses with power breakers is not an option.
Also, is there a good article on how to read transformer damage curves?
Thanks.
c
If i use a 150E fuse the inrush is no longer a problem but the transforer damage curve is worse and arc flash hazard increases a level.
My thought is that the inrush will not occur all the time and is only a theortical value that has the potential to occur. Is there any industry standard i can reference to make a decison on which to sacrifice (nusiance inrush tripping or arc flash and transformer damage). Replacing the 5kv fuses with power breakers is not an option.
Also, is there a good article on how to read transformer damage curves?
Thanks.
c