Hi All,
I was having a quick look at a problem relating to a smallish distribution transformer inrush current, causing a large volt dip on a network voltage, and i'm not sure I believe the results i am getting. The scenario is fairly simple
Grid voltage = 11kV
Grid 3Ph short circuit level = 95MVAsc (5kA)
Transformer rating = 5MVA
Inrush multiplier = 8x
So my calculation is:
Tx inrush power = 40MVA
Vdrop = (40 / (40+95)) *100
Vdrop = 30% !!!
I'm neglecting any remenant flux, and assuming that the transformer is energised at the worst case i.e. zero votlage crossing.
I have access to ETAP and modelled the system using the transient stability module as a switched inductive load - which gave me very similar results. But I appreciate that to do thes studies properly you need to use something like EMTP or PSCAD. But, overall i'm pretty sure the simple calculation is right, as in principle its similar to a motor starting calculation - but the results don't seem to make sense.
If the calculation is correct, is there a standard easy way of resolving the issue. It's only an 11kv system, so we can't use any fancy techniques like point-on-wave switching.
I was having a quick look at a problem relating to a smallish distribution transformer inrush current, causing a large volt dip on a network voltage, and i'm not sure I believe the results i am getting. The scenario is fairly simple
Grid voltage = 11kV
Grid 3Ph short circuit level = 95MVAsc (5kA)
Transformer rating = 5MVA
Inrush multiplier = 8x
So my calculation is:
Tx inrush power = 40MVA
Vdrop = (40 / (40+95)) *100
Vdrop = 30% !!!
I'm neglecting any remenant flux, and assuming that the transformer is energised at the worst case i.e. zero votlage crossing.
I have access to ETAP and modelled the system using the transient stability module as a switched inductive load - which gave me very similar results. But I appreciate that to do thes studies properly you need to use something like EMTP or PSCAD. But, overall i'm pretty sure the simple calculation is right, as in principle its similar to a motor starting calculation - but the results don't seem to make sense.
If the calculation is correct, is there a standard easy way of resolving the issue. It's only an 11kv system, so we can't use any fancy techniques like point-on-wave switching.