Transformer K-factor Method.

Status
Not open for further replies.

EAntoun

Electrical
Jan 20, 2014
2
Hi,

I'm sizing a 1500 KVA transformer and I need some assistance to determine whether it need needs to be a K-type or not.

The MCC fed by the transformer have about 80 HP of VFD load, and around 1000 HP of linear load.

I used some excel sheet calculator to determine my K-factor for the transformer and it shows as [highlight #8AE234]1.2[/highlight] K-factor.

My question is the following:

Is there a need to get a K-4 transformer in this case? or is the k-factor too small to bump the rating to a K-type?
in other words, what is the break point before we would have to consider bumping up the rating.

Please advise if this info is shown anywhere In IEEE standards.

Thanks.

 
Replies continue below

Recommended for you

Without knowing the harmonic content of the input currents to your VFD it's impossible to tell, but lets face it, you've got about 7% of non-linear load; I very much doubt that is ever going to be an issue.

Also, I wish Le Système international d'unités was international :)
 
k factor of 1.0 is a linear load (no harmonics). above 1.0 begins to get non linear. can you post your calc to get 1.2
 
I agree that there most likely will not be a problem unless you are loading the transformer at or near its rating. See C57.110-2008 - IEEE Recommended Practice for Establishing Liquid-Filled and Dry-Type Power and Distribution Transformer Capability When Supplying Nonsinusoidal Load Currents to evaluate the loading if you are loading close to the rating. Non-linear loads cause more heating that linear loads.
 
I also can't see there being a problem with ~80kVA of non-linear load on a 1500kVA transformer with ~1080kVA load total. You're just over 2/3rds loaded on the transformer.
 