Here at an electric distribution coop, we have always used a guide probably from the old REA days for sizing transformers. I’m wondering, though, why does load capacity go down with more customers?

Example: for a 25 kva transformer, the first column is number of customers and the second is the correlating transformer load:
1 7500
2 8000
3 8400
4 8400
5 8200
6 8000
7 7700
8 7200
9 7200
10 7000

I know as more customers are added (1-4) capacity increases because of more diversity, so why doesn’t the load capacity continue to increase?
I tried looking at the IEEE C57.91 standard, but couldn’t find anything.
 
Replies continue below

Recommended for you

Assuming that the "correlating transformer load" is watts per consumer, it looks like someone tried to use the old REA Bulletin 45-2 Demand Tables nomograph for kW demand with about 1700 kWh/mo/consumer and extrapolate below 5 consumers. This method is for many customers on a feeder, not for transformer loading. The extrapolation may explain why the watts/consumer does not follow the expected pattern below 5 consumers; the nomograph stops below 5 consumers.
 
To clarify, the second column is in kWh.

The kWh for 1 consumer also doesn't increase linearly:

First column is transformer kva size, the second is kwh, and again this is for just 1 consumer:
3 300
5 500
7.5 1000
10 2500
15 4000
25 7500
37.5 12500
50 16000

Does this guide assume different load factors?

Thanks in advance for helping me sort this out.
 
Kayto
I think your chart is wrong. Assuming the customers are similar in their load, the load per customer would be the same. However, when you add more customers to a transformer the diversity of load occuring at any monent does not follow a straight line. The chart should look something like the following:

1 7500
2 8000
3 8400
4 8600
5 8800
6 9000
7 9300
8 9500
9 9800
10 10000

 
I'm not sure where your chart is from, but I calculate a loading based on the house sq ft and construction, and use a diversity factor for each transformer - the more consumers you connect to one transformer, the less transformer kva you need because the load diversifies - not everyone is at peak load at the same time. Add up the calculated peak loads for all houses on a transformer and multiply by the DF to get transformer kva

# of houses DF
1 1
2 .86
3 .78
4 .73
5 .69
6 .67
7 .65
8 .63
9 .62

Also, most transformers can be loaded to 140% of nameplate. This will shorten the life of the transformer some and losses are higher.