bettoni

Electrical
Mar 14, 2002
5
I´m working with EPRI´s PTLOAD program for a Transformer and Autotransformer Loadability Study. The software asks me to put the following features:

No load-core- loss
Load loss for an operating point -for instance nominal load-

I´cant get the information about these values, the manuals I´ve got are incomplete,some are very old. Can someone show me if there´s a method of estimating the losses, if the fenomenon can be linealized to obtain the values at any load level within a determined margin? Is there also any loss comparation method between transformers?

Thanks for your time.
 
Replies continue below

Recommended for you


IEEE C57.12.10 lists ranges of impedance for various transformer sizes, and IEEE C57.12.90 describes tests for measuring copper and iron losses. Transformer after-production test reports are the usual source for precise numbers.
 
Hello,

I know that there is a very close relation between X/R ratio and copper losses.
In some cases, it is easier to obtain the X/R ratio for transformers than copper losses.

In IEEE red book there is a graphic to obtain X/R ratio (approximated!) for transformers with different ranges.

Regards
 